February 17th, 2020 11:38 AM #121
Sir Travs, I'll ask the electrician if he still pull a wire, but the way I saw it, it looks like he can't because I think he used mica tube embedded on the beam up there.
Sir Walter, I hope I noticed this earlier, problem now is the whole wall is already tiled.
-
February 17th, 2020 11:40 AM #122
Sir Travs, all of my outlets are universal 3 prong and have ground wires, of all outlets, the electrician had to miss this one
-
February 17th, 2020 11:47 AM #123
-
February 17th, 2020 12:04 PM #124
They are all installed Sir Travs, will tapping a ground wire to the concrete do, or it really needs to be tapped to a rebar?
-
February 17th, 2020 12:07 PM #125
-
February 17th, 2020 12:17 PM #126
-
Tsikoteer
- Join Date
- Nov 2009
- Posts
- 3,507
February 17th, 2020 12:19 PM #127You have to run separate ground wire minimum AWG#10, should be earth bonded. If no existing grounding system there are available copper or GI grounding rod, maybe a 5ft will do depending on your location.
I use aircon plug, the 20A version, or if your heater is rated 3.5KVA you may use the standard Panasonic 16A 3-prong. Make sure to identify/tag the circuit breaker on the panel board. My 3.5KW single-point heaters uses 15A circuit breaker, no problems for 20yrs.
-
Tsikoteer
- Join Date
- Nov 2009
- Posts
- 3,507
February 17th, 2020 12:28 PM #128Yes sure, just check if the ground is good. Using the AC Voltmeter, a typical balanced transmission(in the Metro) should give you 120-0-120V line to ground to neutral. On unbalanced system(Provinces) it should be 0-230-0. You may use an earth tester or Megger but that would require you a good reference ground, the test i provided above should be enough to make sure leakage current would go on that ground path instead of your body. If still unsure, you could double protection using GFCI and AFCI ckt breakers.
-
-
February 17th, 2020 01:38 PM #130
GFCIs will give some added protection on wet areas like kitchens, baths, garages & outdoor outlets. However, Installing an outlet w/o the 3rd earth wire will NOT provide a ground path for three wire grounded devices. 2wire GFCI app will only provide protection against ground fault.