Update to my issue:
Binalik ko sa CarTech service center and they were firm na hindi na daw kaya ng compressor yung freon spec amount na 400g. At hindi din daw sila nag totop up ng compressor oil. Dapat full flush daw yung gagawin which costs around 6K. They tried bringing it up to 400g again pero ganun parin talaga.
I brought it to Coolmate thinking na magiging mga 2K lang din yung freon recharge plus compressor oil top up. The discounted quote I got was 3K when I was there. Nag go na ko and recharge nila to 400g plus 40cc's of oil directly put sa compressor. Nawala significantly yung noise and it looks like my problem is solved. O-ring lang talaga cause ng leak.
Lesson learned talaga dito na hindi "it's all the same" ang mga gumagawa ng aircon. Na doble gastos ko because of that. Kung from the start pinagawa ko na sa EEB Aire (malayo nga lang kasi from my residence) na 1.8K lang ako kasama na freon recharge, o-ring replacement, and compressor oil top up dun.
Also, walang kwenta ang CarTech service center Taguig, hehe. I'll never go back to that shop.