Quote Originally Posted by CVT View Post


Bro.,- 1HP=746W- for simplicity.- let's put it at 1KW or 1KVA - so for every 1HP comprehending starting current (x3)- plan for 3KVA capacity.

So, for your factor of safety for motors with huge starting current,- then your 22KVA can support 7HP total, probably more, but you can experiment and monitor, as this is on the very safe side... Lighting,- not much load so this is your extra 1KVA.....(22/3 = 7 remainder of 1)

19.4K:tomato:
Kung gusto mo sir na mamaximize ung 22kva genset mo sir palitan mo ac mo ng inverter type. 1:1 na ang computation nun at no starting current. Pero pagkakaalam ko ang starting current ng single phase equipment is similar lang the Full Load Ampere (FLA) sa 3phase lang ung times 3.