Originally Posted by
oj88
I'm interested to find out what kind of UPS they were using. For something that is classified as critical infrastructure, I'm sure they're the online double-conversion types. But I can't understand how a failed fan/blower took down everything. These UPSs have bypass modes.... which should address any internal faults that may have developed within the UPS.
Getting 380V instead of 220-240V is a wiring and/or possibly a configuration issue, not a power surge. Most large datacenter UPSs are 3-phase. So it would seem that while they were panic-stricken trying to put everything back online, they powered the 220-240V equipment directly from 380V, which is one of the standard Line-to-Line voltage of a 220V/380V 3-phase source. You get 220V from Line-to-Neutral, in this case.
I think they're playing the blame game to minimize their own failures, pointing a finger at Meralco for the "power surge". If that were actually the case, it would've affected everyone in the neighborhood, not just CAAP.