No need to buy a phase converter.. Iba ito sa iniisip mo.
Bro.- 3phase - 3 sinusoidal waves iyan na 120deg off phase sa isa't isa,- kaya walang time na zero ang voltage - pang machine application.
Bro.,- Puwedeng line to line or line to neutral(kung WYE configuration) ang kunin mong linya (isa ito sa 3 sinusoidal wave)... Pero,- tama ba ang voltage nito sa iyong requirement? A multimeter set to VAC should be able to give you the effective voltage level... However, the frequency should be spec'ed on your genset.
Typically line to line voltage is 1.73 x line to neutral voltage. (1.73 is square root of 3)
I assume may ground iyan... i measure mo rin ang line to ground voltage.
Else, kailangan mo ng step up or step down transformer,- whatever is appropriate.
19.4K:tomato:
Last edited by CVT; June 6th, 2013 at 10:42 AM.
Bro., simple lang (di ba ME ka ng mahal nating Berde?)...
1. Get a multimeter and set it to VAC (voltage - AC)
2. 3-phase iyan so tatlo ang ports or "lines"
3. Connect your multimeter probes in 2 of those terminals
4. It should read 220V for you to able to use it in your house.
5. If 220V - then connect those two ports you just measured to your house electrical line. You should be okay
6. If not - say 400V - you need a stepdown transformer to bring it down to 220V - take note of the power requirement of your house - 5KVA/W for example
7. If not - say 110V - you need a step up transformer to bring it up to 220V - take note of the power requirement of your house - 5KVA/W for example
8. Frequency - read it from the manual or the plate on the genset - should be 60Hz. If not you need a frequency or phase converter.
19.4K:tomato:
Di ba nagkaka uneven load sa genset if 2 terminals/lines lang ang gagamitin ko?
240V ang voltage ng genset.
And if 2 terminals/lines lang gamitin ko, tama ba na hindi na full capacity ng genset ang magagamit ko?
Signature
Uneven loading should be the least of your worries bro.
Actually, ginagawa iyang load balancing ng power distribution companies....
Yes,- hindi full capacity ng genset dahil iyong dalawang phases,- walang load,- wasted energy pero minimum lang dahil nga walang load.... Your new capacity is full capacity of genset divided by 1.73.
Ano ang full power capacity ng 3-phase genset mo?
Important na 60Hz iyan,- else delikadong gamitin ang aircon, ref at ibang motors sa bahay.....
19.4K:tomato:
Last edited by CVT; June 6th, 2013 at 11:07 AM.
45kva.
Sabi kasi ng electrician masisira daw dynamo if uneven ang load.
Signature
So if my genset is 45KVA and I'll just use one phase, what's the equivalent capacity that I can utilize from the genset?
Right now, my genset supplies the following:
1 phase to my office
1 phase to our dirty kitchen/dining/maid's quarters/workers' quarters
1 phase to the house.
Lilipat ko na kasi office ko so mawawalan\ ng load sa office. Mababawasan din yung load sa isa kasi lilipat din workers' quarters.
Signature
Ito phase converter sir boybi.. baka pwede reversible yan 3phase in and 1phase out.
Rotary Phase Converter Philippines - 12392041
Ginagamit mo na pala na parang single-phase e... Ganyan din ang ginagawa ng mga power distributors... Iba't iba ang phase na ginagamit ng mga bahay for a more balanced loading for power saving...
The maximum capacity of one phase (line to line) = 45/1.73 = 26KVA....
19.4K:tomato:
Last edited by CVT; June 6th, 2013 at 12:47 PM.
So ok lang mawalan ng load yung isang phase then mabawasan pa yung isa pang phase. So di ko na pala need ipa-reconfigure itong wiring ng genset ko.
Signature
^
baka lang sir boybi na reversible input and output lang naman yan or they might have a 3phase to 1phase na phase converter. naki singit lang nug bata. give them a call na lang sir.![]()
^
pwede nga sir boybi yan ung sinabi ko nung una na line 12 or 23 or 31 na makakakuha ka ng 230v dyan na 1phase. wag lang masyado malaki voltage unbalance kung hindi iinit transformer.![]()
Tinakot kasi ako ng electrician, dapat daw balance sa lahat ng phases ang load.
Signature
^
worst thing that could happen if unbalance ang load is iinit ang transformer at rated load/capacity. pero mababa naman load mo sir boybi, it should be no problem.
Ilan aircon ba ang kaya ng 22kva? May 1hp pa na water pump and refrigerators. Plus mga ilaw.
Signature